Guest Firediver

SAFETY INFO - Solar Panels - A MUST read!

21 posts in this topic

This is an e-mail I received and FYI that should be passed around to EVERYONE in the fire service. If anyone has anything else to add to this please do. But please give FIRST hand knowledge and not what you heard from a friends mothers brother. Thanks :lol:

Tony Tricarico

Captain - Squad Company 252

FDNY - Special Operations Command

At this past Monday's Twp. Chief's meeting, I went to the presentation put on by the State of NJ last night at Amwell Valley Fire concerning solar panels and the danger they present to the Fire Service.

The presentation lasted for about 2 1/2 hours and was what I believe time well spent. It really opened my eyes to the potential danger and problems they will be for us for any dwelling fire we will encounter where they are present. I'm going to attempt to give everyone a quick snapshot of what was covered.

The thing to know with solar panels are that they cannot be shut down - they are ALWAYS ENERGIZED. And they are energized with up to 600 volts of DC current. For example, you cannot put an ax through them to open up a roof to vent - your putting the ax through 600 volts. If fire is infringing upon solar panels on the roof it will compromise the integrity of the panels. You then have 600 volts of live electrical energy - and what don't you do when you have live electrical energy? - you don't put water on it. Even if the roof burned through and the panels fell into the structure, unless the panels were destroyed (de-energized) by the fire and/or falling into the structure, they can still have the potential to be live,they have to be treated as such and have the potential of 600 volts of DC current.

A basic solar system consists of: The solar panels themselves; a combination box; a disconnect box; and a inverter. The panels all feed into a combination box. The combination box (which is almost always located on the roof) takes in all the energy and sends it to a disconnect box. The disconnect box takes the energy and then sends it into the inverter which converts the DC current into AC current. From there the AC energy "pushes" into the structure's normal electrical system.

The combination box has fuses in it that come from the solar panels themselves. If you access that box, you can pull all the fuses inside and "kill" anything after the combination box. But remember the panels are still live and have up to 600 volts in them. If you "kill" the energy at the disconnect box - anything up to that box is still energized - the solar panels, the combination box, the line going from the combination box into the structure and into the disconnect box are all still energized. The power company pulling the meter for normal service has no effect whatsoever on the solar panel system - it is all still live and has up to 600 volts of DC current. The only "good" thing when it comes to the disconnect box and the inverter is that they need to be co-located with the normal service panel for the structure and each should be marked as appropriate.

Even if it's nighttime and the solar panels have not been exposed to direct sunlight for several hours, they still are energized and can kill you. It is estimated that the panels would need to be covered with an opaque tarp for 7-10 days before the panels will "de-energized" down to minuscule levels. (although the handouts specify that this is an option for safety steps - it is not accurate per the presenter)

In closing there are people who have greater minds and resources than we do in developing a process to safely handle fires which may involve these systems - such as the NFPA, OSHA, etc. Per the presenter, the situation - and these organizations, are now starting to become aware of the potential problems. So far in the State of NJ, there is no recorded injury to a Firefighter being caused by coming into contact with a solar panel system. Ironically, New Jersey comes in 2nd when it comes to solar panel system installations in the nation, behind Califorina.

The final question which was asked really put things in prospective - someone asked that since Califorina is number one when it comes to Solar Panel Syatem installations, "...what do their Firefighters do when a structure fire involves these systems?" Answer was "... they let it burn!"

Please, I'm not suggesting that we adopt this strategy. But the reality is - I really don't have an answer and it seems as if the Fire Service industry, nor the Solar Panel Companies, don't either.

Just - please be aware and please be careful if you roll up to a structure where a solar panel system is installed - bottom line, if can kill you.

Share this post


Link to post
Share on other sites



Good information. Thanks for sharing. Just something else for us to think of when arriving on scene. I know of a few places off the top of my head in my district where there are solar panels, and I never really thought of them as a hazard before.

Share this post


Link to post
Share on other sites

Please get this information to your chiefs and asst chiefs fast---I will be adding it to all my classes just to get the message out.

Thanks for the information

Share this post


Link to post
Share on other sites

Thanks for the information just another item in the preplan and size up checklist

Share this post


Link to post
Share on other sites

Just received an email on this that stated not all solar panels are electric some are just for heating water and is hot to touch on a sunny day but no electrical current. Can anyone confirm or deny this??????

Share this post


Link to post
Share on other sites
Just received an email on this that stated not all solar panels are electric some are just for heating water and is hot to touch on a sunny day but no electrical current. Can anyone confirm or deny this??????

Yes hot water systems are out there. They have piping hooked to water storage tanks or circulating pumps to heating systems or swimming pools. They are not connected to the electrical system.

Share this post


Link to post
Share on other sites
Just received an email on this that stated not all solar panels are electric some are just for heating water and is hot to touch on a sunny day but no electrical current. Can anyone confirm or deny this??????

Solar water heaters:

My brother in MA has some on his house - no electrical current.

post-8519-1230912023.gif

http://apps1.eere.energy.gov/consumer/your_home/water_heating/index.cfm/mytopic=12850

Share this post


Link to post
Share on other sites

How can you tell the difference?? and if you cant please treat them as live!!!

Share this post


Link to post
Share on other sites

There are also oil based systems. My limited experience with your typical residential solar panels has them not being nearly as dangerous as these bulletins that keep coming out make them out to be. It'd be nice to see some detailed training that really covered all aspects of solar panels.

Share this post


Link to post
Share on other sites

I've been considering adding solar panels to my house for some time. Some research shows that the amount of energy you produce can be introduced into the grid and the electric company will pay you for it as you pay for it now. However expensive they are, using renewable energy sources is important too. I think a solution would be that town's require homeowners to notify the building department and the fire department upon installation so that they are aware of it prior to an incident.

Share this post


Link to post
Share on other sites
I've been considering adding solar panels to my house for some time. Some research shows that the amount of energy you produce can be introduced into the grid and the electric company will pay you for it as you pay for it now. However expensive they are, using renewable energy sources is important too. I think a solution would be that town's require homeowners to notify the building department and the fire department upon installation so that they are aware of it prior to an incident.

NYS Law requires a building permit to install them. So the building dept. must not only be notified, but also inspect the final install.

In New Rochelle the building dept has already issued stop work orders and the courts have fined contractors for failing to get a permit.

Share this post


Link to post
Share on other sites

Well I guess that is a good thing...didn't get that far yet...still trying to figure out cost-benefit/risk numbers...don't know anyone in particular who has them yet.

Share this post


Link to post
Share on other sites

While we didn't originally send anything about this on The Secret List, we did have some information that was sent to us as a submission that we posted on the website-and the info was inaccurate. Many of your probably saw the e-mail "floating around" on the "solar panel" issue as well. Due to the amount of submissions that come into www.FireFighterCloseCalls.com, it is impossible to not have something slip through once in a while, albeit rarely. We have always taken technical accuracy extremely seriously since we started The Secret List and the FFCC website 11+ years ago and we do our best.

We are fortunate and appreciative to have alotta readers. One of them is a San Jose (CA) FF. A FF who teaches classes on FF Safety related to PV (photovoltaic) systems, who has a degree in Solar Technology, and is also a member of the California State Fire Marshals PV Task Force. While we heard from many in the manufacturing community about this issue, we were very glad to hear from Fire Engineer Matt Paiss of the San Jose FD who wanted to offer some "firefighter" clarity to this discussion. It is an area we all need to be aware of, but as is often the case; a few misconceptions can create miscommunication.

We will turn this over to Matt so he can provide his training and knowledge to address the issues one by one so you can develop your own FD SOP:

1. Panels are only energized in daylight. Overcast days too, but NEVER at night. Scene lights will NOT energize the panels.

2. If the panels, or the roof are on fire, you will not get shocked by spraying water on them. Put the fire out.

3. The voltages of panels are anywhere from 24-48 volts each and generate from 125 to 200 watts in optimal conditions.

These panels are "strung" together in series to increase the voltages to 120 vdc to 400 vdc. While 600 vdc is possible, it is pushing the UL ratings of the enclosures, etc.. The current of these strings is usually from 5-9 amps. And that is only when there is a load (or put more simply, the inverter is sending the power back into the grid). If the inverter is off, there is no current only voltage, i.e. open circuit.

4. The inverters that change the power from DC to AC, are powered by AC. If you shut off the main service breakers, the inverter is OFF and there is NO AC power being sent into the structure. There are capacitors in the inverters that can hold a charge for about 5 min, but in the daytime the panels are producing power anyway. When the sun goes down....everything is de-energized.

FIREFIGHTER WARNING:

There is ALWAYS energized DC power in the conduit from the panels to the inverter IN THE DAYTIME. So, secure all utilities (per SOP's) and stay away from the panels and the conduit in the daytime. That is the danger.

5. Do not break a panel with your axe or related forcible entry tools. Each panel in the string could be carrying the FULL VOLTAGE of that string (120-400 VDC), not just one panel, so if you put a tool through it, you will very likely be getting the rest of the shift off....so don't do it....there is no need to do it, vent somewhere else, and kill the utilities at the main panel based upon your SOP's.

6. There are often junction boxes on the roofs (residential systems). If they do have fuses (not all do), and you pull a fuse while under load, you will very likely cause a fire. Not to mention the time it will take to open the box and do this. Bad idea-leave it alone.

7. In California, we will not let a house burn because it has PV Panels on the roof. I may not be able to put my hole in the best place, but I will put one in where I can when required.

Thanks Matt.

If you have any questions or comments for Matt, he can be reached thru our submissions page:

http://firefighterclosecalls.com/submit.php

Firefighters and Officers should do their best within their own FD SOP's, to know where in their 1st due area they have these panels...thru pre-planning. Once they are identified, determine the plan before the fire and do followup thru the installer/mfg of the panels. We will also have links to a video and related info posted soon so you can further learn and followup

posted from the secretlist from firefightersclosecalls.com

Share this post


Link to post
Share on other sites

Thanks for adding that Mark

Share this post


Link to post
Share on other sites
Thanks for the information just another item in the preplan and size up checklist

Can you think of any houses in our first due with solar panels??? :o

That is good - eye opening info!

Share this post


Link to post
Share on other sites

Dan maybe not first due but maybe close to first due, how about the Carey Institute for Ecostudies on the Sharon Turnpike (44A) in your own stomping grounds of Millbrook.

http://www.ecostudies.org/index.html

Share this post


Link to post
Share on other sites

Yes indeed...but there is a 2 story wood frame right across from the gas station between Cumberland Farms and Four Brothers - steep pitch roof and a huge solar panel on top.

Share this post


Link to post
Share on other sites

Yes indeed, the tax man with the same last name as 36-2.

Share this post


Link to post
Share on other sites

Funny this came up, recently I was at a structure fire operating as the FASTeam and ran into solar panels on roof of a 1 1/2 story wood frame. It was upon my initial size-up/walkaround, I immediately transmitted it to the IC and we soon determined that they were in fact for heating the water. But there is still a hazard even if they're not energized, they still are a dead load on the roof. At this particular incident the main body of was pretty much directly underneath them so the interior crews had to use caution while operating in the attic.